Click PLC run time log?

Created Date: October 23,2016

Created By: JCM78

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Click PLC - What is the best way to be able to record or log the run time of an output? I have run time bit of c111 in parallel with my Y1 out put and i just want to keep track of the time it runs. I would also like to display that time on the HMI (cmore EA3-T6CL). If i use a regular time it will just display hours,minutes,seconds, etc. Is there a way to display on the HMI Fan (c111) has run for a total of xx:xx:xx Thanks


  • adccommunitymod (AutomationDirect)

    Created Date: October 23,2016

    Created by: JCM78

    Click PLC - What is the best way to be able to record or log the run time of an output?

    I have run time bit of c111 in parallel with my Y1 out put and i just want to keep track of the time it runs.

    I would also like to display that time on the HMI (cmore EA3-T6CL).

    If i use a regular time it will just display hours,minutes,seconds, etc.

    Is there a way to display on the HMI Fan (c111) has run for a total of xx:xx:xx

    Thanks

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 23,2016

    Created by: kewakl

    The click doesn't have any native time management abilities (other than the simple RTC properties) so you might count RUN time seconds and math out the hr:mn;sc to three DS registers and send to three numeric displays on the EA3.

  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2016

    Created by: JCM78

    I cant even get my fan timer t3 tag to show up so i can put it in a text display box.... My therms df1 & df1 display correct in the text box. Any idea what im doing wrong?

  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2016

    Created by: winterrossi

    You have to copy the timer accumulator to a DS register. Then read the DS value from the C More.

  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2016

    Created by: kewakl

    I cant even get my fan timer t3 tag to show up so i can put it in a text display box.... My therms df1 & df1 display correct in the text box. Any idea what im doing wrong?

    You have to copy the timer accumulator to a DS register. Then read the DS value from the C More.

    Change the cmore tag datatype to Signed 16-bit and you should see TD in the Memory Type field.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2016

    Created by: JCM78

    thanks i was able to get that working, is there a way to change a timer setpoint from the c-more?

  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2016

    Created by: kewakl

    thanks i was able to get that working, is there a way to change a timer setpoint from the c-more?

    If you us a DS register for the setpoint.

    I usually allocate the first 50 or so DS registers for Timer presets. This allows a 1-to-1 relationship between a timer number and its preset. no math/thinking involved.

    Then the next 15-30 for counter presets.

    Expand Post