Weintek HMI to Click PLC communication setup

Created Date: August 14,2016

Created By: agbitaw

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Please I need assistance in programming my weintek MT8050ie to communicate wit Click PLC


  • adccommunitymod (AutomationDirect)

    Created Date: August 14,2016

    Created by: agbitaw

    Please I need assistance in programming my weintek MT8050ie to communicate wit Click PLC

  • adccommunitymod (AutomationDirect)

    Created Date: August 14,2016

    Created by: kewakl

    I don't know if Weintek has a Click driver, but Click supports Modbus (RTU - for serial and TCP for Ethernet)

    Try a Modbus driver.

    Then, open the CLICK software, open Address Picker. Click the checkbox for 'display MODBUS Address. '

    I don't have any Weintek-branded HMI's so I won't be much help beyond this.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 14,2016

    Created by: andremholmes

    Look under KOYO electronics from list of PLC type, it has Click and Click Ethernet.

  • adccommunitymod (AutomationDirect)

    Created Date: August 18,2016

    Created by: TISON

    Modbus RTU has worked for me on the DL05, DL06. P-2 series works with RS-232, RS-485, and Ethernet. I have never tried the Click, but the Weintek has lots of choices.

    Good Luck