adccommunitymod (AutomationDirect) asked a question.

EA1-T6CL to Micrologix database help

Created Date: September 10,2015

Created By: BigLou

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I'm interested in trying out AD's EA1-T6CL software to possibly incorporate into future projects. I set up a new project with a Micrologix DF1 full duplex PLC. I want to buld a sample tag database, but keep getting an error: PLC Address Invalid:GUI-024. I put in all the correct information. Under Tag Information, I enter the tag name and data type as 16-bit unsigned, then PLC data type as 'N ', then N7:0 as the address, but I get the error. What am I missing? Thanks, Lou


  • adccommunitymod (AutomationDirect)

    Created Date: September 10,2015

    Created by: bcarlton

    In the 'Address ' leave off the 'N '.

  • adccommunitymod (AutomationDirect)

    Created Date: September 10,2015

    Created by: BigLou

    Got it. Thank You

  • adccommunitymod (AutomationDirect)

    Created Date: September 10,2015

    Created by: BigLou

    I'm interested in trying out AD's EA1-T6CL software to possibly incorporate into future projects. I set up a new project with a Micrologix DF1 full duplex PLC. I want to buld a sample tag database, but keep getting an error: PLC Address Invalid:GUI-024. I put in all the correct information. Under Tag Information, I enter the tag name and data type as 16-bit unsigned, then PLC data type as 'N ', then N7:0 as the address, but I get the error. What am I missing?