adccommunitymod (AutomationDirect) asked a question.

Retentive Memory Question

Created Date: May 08,2015

Created By: trimixdiver1

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I set my EA9 up to use a text entering field to a retentive address on the cmore. I entered text and after a POR it didnt retain the text. Am I doing something wrong? Should I store the info on my DoMore instead? Thanks


  • adccommunitymod (AutomationDirect)

    Created Date: May 09,2015

    Created by: plcnut

    You need to store the value in DoMore, because the PLC is overwriting the value the Cmore is trying to save.

  • adccommunitymod (AutomationDirect)

    Created Date: May 11,2015

    Created by: mwdkmpr

    I stopped using internal tags a long time ago because retentive is not always retentive. I do not what a POR is but I know all internal tags are cleared with a download to the panel. Do as plcnut says and save them to the PLC where retentive is retentive.

  • adccommunitymod (AutomationDirect)

    Created Date: May 08,2015

    Created by: trimixdiver1

    I set my EA9 up to use a text entering field to a retentive address on the cmore. I entered text and after a POR it didnt retain the text. Am I doing something wrong? Should I store the info on my DoMore instead?

    Thanks