Has anyone connected an06 to a Watlow ex-zone controller? I am trying to communicate through port 2 on my 06 to an EZ-Zone controller that has Modbus communications. I am trying to pull the input values from th eWatlow controller to my 06. Any help would be appreciated. Paul Ribich
Created Date: April 09,2013
Created by: techme
06 to Watlow EZ Zone
It looks like the value you want to read is at Modbus address 360 in the Watlow controller and the value is a Floating point data type. If you are using the MRX command you would have the following:
Port # :K2
Slave address: K ?? ( Whatever your Watlow address is set to.)
Function Code: 03- Read Holding Registers
Start Slave Memory Address: 40360 ( 360 per the EZ Zone manual)
Start Master Memory Address: V????(wherever you wish it to go reserve 2 words)
Number of elements: K2
584/984 data format
change Exception response buffer to a unique address.
Since it is a floating point I am not sure what order it will come in. ( low word/ high word or high word/ low word) but it looks like there are provisions in the Watlow controller to change the order if needed.
Created Date: April 05,2013
Created by: psribich
Has anyone connected an06 to a Watlow ex-zone controller? I am trying to communicate through port 2 on my 06 to an EZ-Zone controller that has Modbus communications. I am trying to pull the input values from th eWatlow controller to my 06.
Any help would be appreciated.
Paul Ribich