adccommunitymod (AutomationDirect) asked a question.

06 to Watlow EZ-Zone w/modbus

Created Date: April 05,2013

Created By: psribich

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Has anyone connected an06 to a Watlow ex-zone controller? I am trying to communicate through port 2 on my 06 to an EZ-Zone controller that has Modbus communications. I am trying to pull the input values from th eWatlow controller to my 06. Any help would be appreciated. Paul Ribich


  • adccommunitymod (AutomationDirect)

    Created Date: April 09,2013

    Created by: techme

    06 to Watlow EZ Zone

    It looks like the value you want to read is at Modbus address 360 in the Watlow controller and the value is a Floating point data type. If you are using the MRX command you would have the following:

    Port # :K2

    Slave address: K ?? ( Whatever your Watlow address is set to.)

    Function Code: 03- Read Holding Registers

    Start Slave Memory Address: 40360 ( 360 per the EZ Zone manual)

    Start Master Memory Address: V????(wherever you wish it to go reserve 2 words)

    Number of elements: K2

    584/984 data format

    change Exception response buffer to a unique address.

    Since it is a floating point I am not sure what order it will come in. ( low word/ high word or high word/ low word) but it looks like there are provisions in the Watlow controller to change the order if needed.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 05,2013

    Created by: psribich

    Has anyone connected an06 to a Watlow ex-zone controller? I am trying to communicate through port 2 on my 06 to an EZ-Zone controller that has Modbus communications. I am trying to pull the input values from th eWatlow controller to my 06.

    Any help would be appreciated.

    Paul Ribich