Hello, We have a 8 foot tall tank and would like to record the level of the tank back to the HMI. Any recommendations on level switches to accomplish this? Thank you.


  • adccommunitymod (AutomationDirect)

    Created Date: October 16,2012

    Created by: johnaden

    Do you need a continuous readout, ie percentage, etc., or just a few discrete points?

  • adccommunitymod (AutomationDirect)

    Created Date: October 16,2012

    Created by: Bob S BN

    Look for Ultrasonic Level Transmitters for continuous variable level sensing. They will require an analog input on the PLC to match though. AD has some in the catalog.