adccommunitymod (AutomationDirect) asked a question.

C-more to Click interface

Created Date: July 11,2012

Created By: JimG

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a control panel built for a water treatment system using a DL-250-1 PLC with a 10 inch C-more touch panel. Part of the system controls the valves for sending the water through 2 filter presses. The filter presses are 2 stand alone system where each is controlled by a CLICK PLC and c-more micro touch panel mounted on each press. The CLICK on each press controls the start and stop functions of the press cycle locally. I would like to perfrom this function remotely from my main control panel with the C-more and keep the local functioning panels as well. How would I set this type of network up?


  • adccommunitymod (AutomationDirect)

    Created Date: July 11,2012

    Created by: Bob S BN

    I'll give you something to look into, although I haven't done this myself.

    You don't say how your talking to the DL250-1, but port 2 has RS-485 capability, and I believe the Clicks do also, as does the C-MORE.

    So, I believe you could create a RS-485 multidrop network to talk to all three of the PLCs from the main C-more.

    Even it you 're talking to the DL250-1 over ethernet, you could still use the Cmore serial port to talk to the CLICKS over RS-485.

    Just something to look into till those that have done this chime in,

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: July 12,2012

    Created by: JimG

    Thanks for the reply. I am going to try that route and see if it works. My C-more panel is using ethernet to communicate with the 250-1. I believe I can set the CLICK's up as DEV002 and DEV003 and make it work.

  • adccommunitymod (AutomationDirect)

    Created Date: July 12,2012

    Created by: Bob S BN

    I believe I can set the CLICK's up as DEV002 and DEV003 and make it work.

    I just did a quick panel manager set up like that, and it took the set up with no errors. I think it should work just fine.

    Be sure to change the "Slave Address " so that both clicks don't have the same one.

  • adccommunitymod (AutomationDirect)

    Created Date: July 11,2012

    Created by: JimG

    I have a control panel built for a water treatment system using a DL-250-1 PLC with a 10 inch C-more touch panel. Part of the system controls the valves for sending the water through 2 filter presses. The filter presses are 2 stand alone system where each is controlled by a CLICK PLC and c-more micro touch panel mounted on each press. The CLICK on each press controls the start and stop functions of the press cycle locally. I would like to perfrom this function remotely from my main control panel with the C-more and keep the local functioning panels as well. How would I set this type of network up?

    Expand Post