adccommunitymod (AutomationDirect) asked a question.
C0-02DR-D and CMORE port 2?
Created Date: May 02,2012
Created By: Benton
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I tried to hook up my cmore panel to C0-02DR-D (analog CPU) in port 2 and it would not communicate with the CLICK ( it kept saying address not the same or that the PLC sent back different function code). Once I swapped it and placed the cmore into port1 it worked fine. The problem I now find is that port2 cannot be used to Write to the PLC. Is there something I can do to fix this?
Created Date: May 02,2012
Created by: Do-more PE
Check your port 2 settings.
Created Date: May 02,2012
Created by: OpZed
When you switch to Click Port2 you'll also need to change the C-more setting in Panel Manager "Select RS485 " from No to Yes.
Created Date: May 02,2012
Created by: bcarlton
Isn't Port 3 the one that uses RS485?
Created Date: May 02,2012
Created by: Benton
Check your port 2 settings.
Thanks for the reply! What do I need to look for in my settings? I made sure that they both have same options selected?
Created Date: May 02,2012
Created by: bcarlton
If you can zip both your Click and Cmore programs and post as attachments.
Created Date: May 02,2012
Created by: Benton
I tried to hook up my cmore panel to C0-02DR-D (analog CPU) in port 2 and it would not communicate with the CLICK ( it kept saying address not the same or that the PLC sent back different function code). Once I swapped it and placed the cmore into port1 it worked fine. The problem I now find is that port2 cannot be used to Write to the PLC. Is there something I can do to fix this?