adccommunitymod (AutomationDirect) asked a question.

Plc-498

Created Date: March 30,2012

Created By: a agnone

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a 6 " c-more connected to a AB MicroLogix 1100. The top banner reads: PLC Code-498 DST Node is out of buffer space. The HMI works just fine, How do I get rid of the message?


  • adccommunitymod (AutomationDirect)

    Created Date: March 30,2012

    Created by: a agnone

    It stopped displaying the banner. Apparently I had pre-assigned tags in the C-More. 5 of the numeric displays were not yet programmed in the MicroLogix PLC. My guess is the C-More was requesting the info for display but the plc could not send it cause it was not in the program yet. Therefore the buffer message. That is very interesting.

  • adccommunitymod (AutomationDirect)

    Created Date: March 30,2012

    Created by: a agnone

    I have a 6 " c-more connected to a AB MicroLogix 1100. The top banner reads: PLC Code-498 DST Node is out of buffer space. The HMI works just fine, How do I get rid of the message?