I am having trouble getting handshaking to work between my cmore hmi and my 250-1 plc. I cant get the right tag to work. any suggestions:confused:
Created Date: December 05,2011
Created by: a agnone
Are you talking about numeric input? How it works is you assign a bit to Notification, lets say C1 and assign C2 to Handshake. You enter a number from the keypad and C1 goes on. It waits for C2 to come on. You have to have something in your ladder that sees C1 and responses by turning on C2. You may have to have C2 stay on for a few milliseconds for the C-More to see it. How are you communicating between the two? You may have to allow for the C-More updating that is why I said you might have to allow some time for the Handshake bit to stay on.