PLC and Panel show different values for same memory location

Created Date: June 30,2011

Created By: syscon

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a DL205 (260 CPU) connected to a EA7-S6M-R panel. A numeric display in the panel is supposed to display the value of a database tag that references V2003 in the PLC but it doesn't. If the value of V2003 is 15 the panel shows 1. When the value of V2003 is 3072 the panel shows about 149. What stupid thing am I doing (or not doing)?


  • adccommunitymod (AutomationDirect)

    Created Date: June 30,2011

    Created by: Steve Bailey

    Sounds like the numeric display in the C-More is scaling the V memory data. Double click on the display object and then look under the "Option " tab to see if scaling is selected.

  • adccommunitymod (AutomationDirect)

    Created Date: June 30,2011

    Created by: syscon

    That's it. Thanks

  • adccommunitymod (AutomationDirect)

    Created Date: June 30,2011

    Created by: syscon

    I have a DL205 (260 CPU) connected to a EA7-S6M-R panel. A numeric display in the panel is supposed to display the value of a database tag that references V2003 in the PLC but it doesn't. If the value of V2003 is 15 the panel shows 1. When the value of V2003 is 3072 the panel shows about 149. What stupid thing am I doing (or not doing)?