adccommunitymod (AutomationDirect) asked a question.
Created Date: January 10,2011
Created By: WolfgangD
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
It appears that programming a C-MoreMicro HMI is quite non-intuitive if the PLC is a WINPLC. I simply cannot figure out how to do the I/O mapping. I have selected the Entivity Modbus RTU protocol for WINPLC, but cannot edit any discrete inputs and ouputs. There is also no reference in the help files (neither in the Think & Do, nor in the C-MoreMicro programming software) as to how to map the inputs and outputs. Where can i find some help?
Created Date: January 13,2011
Created by: HMI Eng
The Help files definitely could be clearer.
The only way to get Think and Do tags into C-more or C-more Micro is to import the MAP file that is created by Think and Do. There is a place at the bottom of the Panel Manager Protocol Setup to Browse and select this file.
Created Date: January 10,2011
Created by: WolfgangD
It appears that programming a C-MoreMicro HMI is quite non-intuitive if the PLC is a WINPLC. I simply cannot figure out how to do the I/O mapping. I have selected the Entivity Modbus RTU protocol for WINPLC, but cannot edit any discrete inputs and ouputs. There is also no reference in the help files (neither in the Think & Do, nor in the C-MoreMicro programming software) as to how to map the inputs and outputs.
Where can i find some help?