adccommunitymod (AutomationDirect) asked a question.
Power outage - hold state
Created Date: October 21,2010
Created By: david222
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I am using a Cmore micro and a DL06 to control feed water pumps to three boilers. The Cmore controls the pumps as far as on / off , auto/ man etc. Everything is on emergency generators. However when power is lost for a brief time all of the pumps have to be restarted thru the Cmore touch screen. Is there a way to have the pumps come back to the position they were at when the power was lost? Thanks David
Created Date: October 21,2010
Created by: JoeW
Depends on your setup and programming, but I assume you are using a toggle switch C Coil to drive a Y Output using the OUT command. You may want to try using SET/RST instead of OUT.
Created Date: October 21,2010
Created by: KPrice
Also, check your retentive ranges in the PLC for the "C " relay. For example, If C1000 is set to be retentive in the PLC, and if C1000 is on before power loss, then C1000 will turn back on after power-up. And if C1000 contact turns on Y0 in your ladder, then Y0 will turn on.
Created Date: October 21,2010
Created by: david222
I am using a Cmore micro and a DL06 to control feed water pumps to three boilers. The Cmore controls the pumps as far as on / off , auto/ man etc.
Everything is on emergency generators. However when power is lost for a brief time all of the pumps have to be restarted thru the Cmore touch screen. Is there a way to have the pumps come back to the position they were at when the power was lost?