adccommunitymod (AutomationDirect) asked a question.
Created Date: July 02,2009
Created By: jgargel
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have a resolution problem on the line trend graph. I am trending a parameter that has a Y-Axis Scale from 0-3000 and a 5 second sample interval with 4 readings to average per sample (so my trend updates every 20 seconds). The actual value of the tag i am trending varies betweeen 1495 - 1505 (which I can see on a numeric display). The trend displays this data as either 1500 or 1470. the resolution is 30 which is 10% of my full scale. If the tag value is 1470-1499 it trends 1470; if the tag value is 1500-1529 it trends 1500. this is pretty useless for a process control application. I have tried changing settings for sample interval and averging, but it makes no difference. Any fixes for this problem?
Created Date: July 02,2009
Created by: marksji
What C-More screen are you using? How big is your trend object? Could your problem be that there just aren't that many pixels on the C-More screen?
Created Date: July 06,2009
Created by: jgargel
Trend Resolution
I am using the largest screen they have - 15 ". The resolution is 1024x768. If my trend height is 500 pixels and my Y-Axis is 3000 units then my resolution should be 3000/500 = 6 units. My actual resolution is 30. It looks like a the C-More limits the resolution to 1% of the Y-Axis scaler.
Created Date: July 06,2009
Created by: Bob S BN
If you know the expected value of the tag, why not narrow up the Y axis to say, 1450-1550?? Odd values will put the line at the limits of the chart, and the value can be checked by touching the chart in the time frame of interest, which will bring up a vertical line to narrow in to a time, and a box with the value and time.
Hope this helps,
Created Date: July 06,2009
Created by: jgargel
The expected value of the tag can be 0-3000; I was just using 1500 as an example of the problem. Touching the screen to bring up the line doesn't help because it displays the same thing as the trend 1470 or 1500 and nothing in between. This is very misleading because the true tag value is never 1470.
Created Date: July 06,2009
Created by: Bob S BN
Perhaps it's because I am logging the data to a CF card, when I use the line to check the data point, the data is accurate, even though the chart doesn't have near the resolution.
Created Date: July 28,2009
Created by: DavL
What version are you using? If you are using 2.42, you may be having a similar issue that I am where the data appeared to be correctly logged to a flash drive but is displayed incorrectly on the trend.
I'm getting ready to create a new thread with full detail of what I have experianced from this and see if others are having the same issue. I'm suspecting a possible bug with the "line graph " objects.
David
Created Date: July 29,2009
Created by: jgargel
V2.41
I am using V2.41. I was told by automationdirect tech support that the line trend object is limited to 1% F.S. For this reason, I can no longer use the C-More touch panels for process applications.
Created Date: July 29,2009
Created by: marksji
I was told by automationdirect tech support that the line trend object is limited to 1% F.S. Wow :eek: That surprises me. Not an issue for anything I'm doing, but I do wonder why they built in that limitation :confused:
Created Date: July 30,2009
Created by: HMI Eng
You said, "the resolution is 30 which is 10% of my full scale " and you also said your full scale is 0 to 3000. 30 is 1% of 3000, not 10%. It looks like you may have realized this in a later post, I just want to make sure.
You are correct, the trend object can only display 1% of full Scale. To display 0.1% would increase the memory required to store the points in RAM by 10 times.
Tell me if I am correct. Ideally the Resolution would be selectable and this selection would determine the Maximum Total Stored Samples. Currently all trends can have up to 65535 Total Stored Samples.
(Just to clarify, the Total Stored Samples is the number of points that can be seen by cursoring back on the trend. This is not the number of points saved to a USB or Compact Flash. This data is stored in RAM)
But is the Resolution also determined the Total Stored Samples, then the memory usage could be limited and higher resolutions could be achieved.
Created Date: July 30,2009
Created by: Steve Bailey
HMI Eng,
I think that suggestion makes the most sense. Let the end user make the best balance between resolution and number of samples for each specific application.