Greetings I was hoping someone has had a similar situation and can point me in the right directly. I have a system with a DL260 cpu, OP-1224 pushbutton panel, connected via a Comm. Master OP-9001. I recently made a change that required that I put the OP-1224 in LED separation mode because two of the buttons would be controlled by either the OP-1224 or a Joystick PB. After this change the OP-1224 locks up when ever the first five LEDs are activated on the OP-1224. The only way to unlock the OP-1224 is to shut off one of the two pieces of equipment that is controlled by another location. I 've done some testing and it doesn't matter which of the 5 leds are off just as long as there are only 4 on the panel doesn't lock up. Here is a list of things I have tried so far with no luck in correcting this issue: Changed addressing in OP-1224 to make sure there was any conflict with that set of bits. (changed from 40600-40607 to 10000-10007) I have replaced the OP-1224 with a new one. I have replaced the OP-9001 comm. master I have changed out the DL260 with a DL250-1 The only other thing I can think of that I haven't changed is the programming. I have looked through the program and haven't seen anything that should conflict with the OP-1224 but as I said I have also tried changing the addressing of the OP-1224 just in case with no luck. If anyone else has come across this type of situation, I'd love to hear what was done to correct it. Thank you in advance.
Created Date: February 17,2009
Created by: HMI Eng
Have you gone back to square one with the original parts and configuration to see if the configuration change caused the problem to begin with?
Created Date: February 18,2009
Created by: neilblue
I haven't tried unchecking LED Separation, which is the original setup for the OP-1224. In theory, if I have it unchecked then setting the bits on or off for the lights in the program shouldn't effect the OP-1224 operation correct? (ex. setting c100 on for OP-1224 addressing range V40600-40607 would turn on the first LED on the top left corner. If you have LED Separation unchecked, c100 would not effect anything at all.)
Created Date: February 16,2009
Created by: neilblue
Greetings
I was hoping someone has had a similar situation and can point me in the right directly.
I have a system with a DL260 cpu, OP-1224 pushbutton panel, connected via a Comm. Master OP-9001.
I recently made a change that required that I put the OP-1224 in LED separation mode because two of the buttons would be controlled by either the OP-1224 or a Joystick PB. After this change the OP-1224 locks up when ever the first five LEDs are activated on the OP-1224. The only way to unlock the OP-1224 is to shut off one of the two pieces of equipment that is controlled by another location.
I 've done some testing and it doesn't matter which of the 5 leds are off just as long as there are only 4 on the panel doesn't lock up.
Here is a list of things I have tried so far with no luck in correcting this issue:
Changed addressing in OP-1224 to make sure there was any conflict with that set of bits. (changed from 40600-40607 to 10000-10007)
I have replaced the OP-1224 with a new one.
I have replaced the OP-9001 comm. master
I have changed out the DL260 with a DL250-1
The only other thing I can think of that I haven't changed is the programming. I have looked through the program and haven't seen anything that should conflict with the OP-1224 but as I said I have also tried changing the addressing of the OP-1224 just in case with no luck.
If anyone else has come across this type of situation, I'd love to hear what was done to correct it.
Thank you in advance.