adccommunitymod (AutomationDirect) asked a question.

Click and HMI

Created Date: January 06,2009

Created By: twbrock

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Will the new Click PLC work with the AutomationDirect EZ-S6M-R touch screen? I have an existing PLC that went bad and I am looking at replacing it with the new Click. Thanks TWBrock


  • adccommunitymod (AutomationDirect)

    Created Date: January 09,2009

    Created by: Tech Guy

    Hello TWBrock,

    Yes, you can use the EZ-S6M-R with the CLICK PLC. Please select 'modicon Modbus RTU ' as the protocol. As you guess, you have to use the standard MODBUS addresses to assign to the objects. This may not be so confortable way. Why don't you try our C-more/C-more Micro HMI panels? With C-more/C-more Micro HMI panels, you can use the CLICK memory addresses (X1, Y2, DS3, DD4...) to assign to the objects. This will make your life easier. ;)

    Regards

    Tech Guy

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 06,2009

    Created by: twbrock

    Will the new Click PLC work with the AutomationDirect EZ-S6M-R touch screen?

    I have an existing PLC that went bad and I am looking at replacing it with the new Click.

    Thanks

    TWBrock