I'm using a 06 and F0-08ADH-1 to measure 0-10 psi using a 4-20ma transmitter. I followed the program in the Options manual on page 4-17, however I need 3 decimal places to display instead of 2. I multiplied by 10,000 instead of 1,000 it won't work. I can get 3 places if I multiply the 2 places by 10, but that always shows a "0 " in the last place. Can this be done on an 06 or would it be better to use a C-more and have it compute the display? The rest of my ladder works fine and I need sto display the psi. I was looking at using a C-more graphics display, am leaning more to a 6 " C-more. Any suggestions?
Created Date: March 28,2008
Created by: bcarlton
I believe that you multiplication by 10000 instead of 1000 is resulting in an intermediate result greater than the accumulator can hold.
Follow the next example, substituting the 10000 for the 1000 as you mentioned. The result can be converted to BCD but the highest result (10000) will need two words.
Created Date: March 28,2008
Created by: wgeckelman
I'll give that a try, figured it might have a number conversion involved. Thanks.
Created Date: March 28,2008
Created by: wgeckelman
I'm using a 06 and F0-08ADH-1 to measure 0-10 psi using a 4-20ma transmitter. I followed the program in the Options manual on page 4-17, however I need 3 decimal places to display instead of 2. I multiplied by 10,000 instead of 1,000 it won't work.
I can get 3 places if I multiply the 2 places by 10, but that always shows a "0 " in the last place. Can this be done on an 06 or would it be better to use a C-more and have it compute the display?
The rest of my ladder works fine and I need sto display the psi. I was looking at using a C-more graphics display, am leaning more to a 6 " C-more. Any suggestions?