adccommunitymod (AutomationDirect) asked a question.

Power Loss

Created Date: February 28,2008

Created By: Engine9991

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am using the EA7-S6C Operator Interface with a 1756-L55 Contrologix controller. I am having an issue when there is a power loss on the operator interface it resets all the numerical entry write tags to zero in the controller after power up. Is there any way around this? I want the operator interface to retain the values already set in the controller. Thanks!


  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: Bob S BN

    I'm not sure about the A-B plc,s (don't want to afford them), my projects are all with AD Koyo plc's. The numeric entry objects display, and can change, the value in the plc memory slot selected from the tag list. The plc is probably where you 're losing the number value.

    That being said, I need to choose in the plc programming software which areas of plc memory are retained during shutdown. Is that an option in the A-B environment?

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: Engine9991

    The tag valvues are retained in the Controller upon power loss to the operator interface. As soon as the operator interface is powered up and establishes communications it resets all values to zero in the controller. It is the operator interface that is writing to these tags.

  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: jackson

    Which driver, exactly, are you using in C-more? Are you using the ControlLogix Tag Driver or are you using the Generic EthernetIP driver?

    If you are using the generic ethernet IP driver, make sure you have the latest version of C-more. There is an option to make your tags retentive in the panel in the newer version. In this driver, the panel is the slave (or server if you prefer) so the panel will zero out it's I data upon power up unless you set them retentive.

    If you are using the tag driver, the panel will not write to tags unless told specifically to (IE.. pushbuttons, numeric entries, recipes, event manager). It will not come up writing to tags by itself.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: Engine9991

    I am using the Generic Ethernet Driver.

    Here is the firmware for the operator interface.

    Hardware: 1400

    Boot Loader: 1003

    Runtime: 1.21.6.18

    System Screen: 1.21.6.18

    The Software Version is 1.21 Build 06.18E

    The software has an option for retentive in the tag editor, but it is greyed out. Only available for internal tags?

    Thanks!

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: Bob S BN

    Newer firmware and software upgrades are available.

    v 2.0 build 07.35 is what I'm at now and it's been a while since I checked the AD tech support site for anything newer.

    Check out the AD site for the free software and firmware downloads.

  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: jackson

    If you get the latest version, you will see retentive tag options in the Panel Manager setting window.

    Also... They have added a ControlLogix Tag driver so this may or may not be more desirable for your application. You are able to import the L5K file from RS Logix and directly reference the tags from your PLC project in C-more. Also this driver is Panel=Client and PLC=Server, more like a traditional HMI to PLC role.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: Engine9991

    That worked! Thanks! For reference, in the panel manager under the PLC protocol there are now more options asking if you would like to use retentive inputs or outputs.

    Thanks for the help!

  • adccommunitymod (AutomationDirect)

    Created Date: February 28,2008

    Created by: Engine9991

    I am using the EA7-S6C Operator Interface with a 1756-L55 Contrologix controller. I am having an issue when there is a power loss on the operator interface it resets all the numerical entry write tags to zero in the controller after power up. Is there any way around this? I want the operator interface to retain the values already set in the controller.

    Thanks!

    Expand Post