adccommunitymod (AutomationDirect) asked a question.

EA7-S6M-R

Created Date: January 18,2008

Created By: kevin91172

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I'm looking for something I can connect 4 DL05 to 1 EA7-S6M-R HMI.I thought i seen one at AD before,or I'm just imagining things?I need it for serial not Ethernet.


  • adccommunitymod (AutomationDirect)

    Created Date: January 18,2008

    Created by: KPrice

    kevin91172, How far is your touch panel from your PLCs? RS485 can go 4000ft end-to-end. I would suggest a RS485 network. Your touch panel would be your master and your PLCs would be the slaves with unique station addresses. Use (1) FA-ISOCON at your touch panel for isolation. And use an FA-ISOCON at each PLC. The ISOCONs include cables for connections to the PLC. If you don't mind making a few solder (or pin) connections, you can make a short cable from the touch panel to the touch panel ISOCON. If you want to go with off-the-shelf terminal blocks, use a straight-through 15-pin cable and a ZL-CMDB15. If you don't want the isolation at the touch panel, you can use the EA-COMCON-3. Hope this helps.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 18,2008

    Created by: kevin91172

    I'm looking for something I can connect 4 DL05 to 1 EA7-S6M-R HMI.I thought i seen one at AD before,or I'm just imagining things?I need it for serial not Ethernet.