adccommunitymod (AutomationDirect) asked a question.

C-More PID faceplate use with Floats

Created Date: December 17,2007

Created By: JulieR

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I can`t seen to use a PID faceplate in the software with the Float type as I keep getting a problem with the minimum or maximum values that are out of range... Can someone help? The PLC will send Floats so I need to use these in the faceplate. Otherwise, I will have to create my own faceplate rather than the ready to use one from the software. My version of C-more soft is 2.0 built 7.35


  • adccommunitymod (AutomationDirect)

    Created Date: December 20,2007

    Created by: HMI Eng

    Can you give more details? What are you doing when you get "a problem with the minimum or maximum values that are out of range... "

    You should call technical support with issues like these. It's Free. 1-800-633-0405

  • adccommunitymod (AutomationDirect)

    Created Date: December 17,2007

    Created by: JulieR

    I can`t seen to use a PID faceplate in the software with the Float type as I keep getting a problem with the minimum or maximum values that are out of range...

    Can someone help? The PLC will send Floats so I need to use these in the faceplate. Otherwise, I will have to create my own faceplate rather than the ready to use one from the software.

    My version of C-more soft is 2.0 built 7.35

    Expand Post