adccommunitymod (AutomationDirect) asked a question.

2 hour oven batch

Created Date: November 01,2007

Created By: kevin91172

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

PLC 06 I am trying to program a 2 hour oven batch timer using 1 60 timer that counts up a minute counter that counts up a hour counter. Next I want to display this 2 hour count down on a EZ-T10C-F HMI.Now how can I not put preset minutes the counter and just put 2 in the hour counter for this thing to work. I am just confusing myself. Any suggestions? The below is just not working for me. // Rung 1 // Address 0 STR SP0 LD K400 OUT V700 LDA O2000 OUT V701 LD K0 OUT V703 OUT V704 OUT V706 // Rung 2 // Address 9 STRN T0 TMRF T0 K1000 // Rung 3 // Address 13 STR T0 LD V3005 BTOR DIVR R4.0949998 RTOB BCD OUT V1400 // Rung 4 // Address 22 STRN T0 TMRF T1 V1400 // Rung 5 // Address 25 STR X30 SET C0 // Rung 6 // Address 27 STR CT1 AND CT3 RST C0 // Rung 7 // Address 30 STRN T1 ANDNE TA1 K0 AND X1 AND V2002 K5000 OUT Y0 // Rung 8 // Address 37 STR V2000 V3002 AND C0 STRN C0 OR T2 TMRA T2 K20 // Rung 9 // Address 45 STR T2 STRN C0 OR CT0 CNT CT0 V5000 // Rung 10 // Address 50 STR CT0 STR CT3 CNT CT3 K3 // Rung 11 // Address 55 STR CT0 STRN C0 CNT CT1 V5002 // Rung 12 // Address 59 STR SP1 ANDN CT3 LD V5000 SUB CTA0 OUT V4000 // Rung 13 // Address 64 STR SP1 LD V5002 SUB CTA1 OUT V4002 // Rung 14 // Address 68 END // Rung 15 // Address 69 NOP #BEGIN ELEMENT_DOC "X1 ", " ", " ", "WE HAVE AIR FLOW " "X2 ", " ", " ", "ELEMENT TEMPERATURE TO HIGH " "X30 ", " ", "TOUCH SCREEN ", "START CYCLE " "X31 ", " ", "TOUCH SCREEN ", "RESET CYCLE " "X41 ", " ", "TOUCH SCREEN ", " " "Y0 ", " ", " ", "HEATERS " "Y1 ", " ", " ", "CYCLE IS DONE " "C0 ", " ", " ", "START CYCLE " "C1 ", " ", " ", "RESET CYCLE " "T0 ", " ", " ", "PID LOOP 1 TIMER #1 " "T1 ", " ", " ", "PID LOOP 1 TIMER #2 " "CT0 ", " ", " ", "Minute counter " "CT1 ", " ", " ", "Hour counter " "CT2 ", " ", " ", "second counter " "V2000 ", " ", " ", "OVEN TEMPERATURE " "V2002 ", " ", " ", "ELEMENT TEMPERATURE " "V3002 ", " ", " ", "OVEN TEMPERATURE SET POINT " #END


  • adccommunitymod (AutomationDirect)

    Created Date: November 02,2007

    Created by: Bob S BN

    If you just need a 2 hour batch counter, did you look at the other timer types available?

    If you choose a "TMRA " accumulating timer, reserve 2 consecutive words for the 8 digit preset and counting areas, you can count for 2,777 hours if needed.

    Much less confusing. Will that work for you?

    Bob

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: November 02,2007

    Created by: kevin91172

    Ok Bob,that will work for me.What will now be an easy way to display on a HMI ____ hours Remaining(V4000) ____ Minutes remaining(V4002)?My code below is not working for me !

    PLC 06

    // Rung 1

    // Address 0

    STR SP0

    LD K400

    OUT V700

    LDA O2000

    OUT V701

    LD K0

    OUT V703

    OUT V704

    OUT V706

    // Rung 2

    // Address 9

    STRN T0

    TMRF T0 K1000

    // Rung 3

    // Address 13

    STR T0

    LD V3005

    BTOR

    DIVR R4.0949998

    RTOB

    BCD

    OUT V1400

    // Rung 4

    // Address 22

    STRN T0

    TMRF T1 V1400

    // Rung 5

    // Address 25

    STR X30

    SET C0

    // Rung 6

    // Address 27

    STR T2

    RST C0

    // Rung 7

    // Address 29

    STRN T1

    ANDNE TA1 K0

    AND X1

    AND V2002 K5000

    OUT Y0

    // Rung 8

    // Address 36

    STR V2000 V3002

    AND C0

    STRN C0

    OR T2

    TMRA T2 V4004

    // Rung 9

    // Address 43

    STR C0

    LD V4004

    SUB TA2

    DIV K600

    OUT V4000

    // Rung 10

    // Address 48

    STR C0

    LD V4000

    DIV K600

    OUT V4002

    // Rung 11

    // Address 52

    END

    // Rung 12

    // Address 53

    NOP

    #BEGIN ELEMENT_DOC

    "X0 ", " ", " ", "TEMPERATURE IS GOOD "

    "X1 ", " ", " ", "WE HAVE AIR FLOW "

    "X2 ", " ", " ", "ELEMENT TEMPERATURE TO HIGH "

    "X30 ", " ", "TOUCH SCREEN ", "START CYCLE "

    "X31 ", " ", "TOUCH SCREEN ", "RESET CYCLE "

    "X41 ", " ", "TOUCH SCREEN ", " "

    "Y0 ", " ", " ", "HEATERS "

    "Y1 ", " ", " ", "CYCLE IS DONE "

    "C0 ", " ", " ", "START CYCLE "

    "C1 ", " ", " ", "RESET CYCLE "

    "T0 ", " ", " ", "PID LOOP 1 TIMER #1 "

    "T1 ", " ", " ", "PID LOOP 1 TIMER #2 "

    "T2 ", " ", " ", "OVEN TIMER #1 "

    "V2000 ", " ", " ", "OVEN TEMPERATURE "

    "V2002 ", " ", " ", "ELEMENT TEMPERATURE "

    "V3002 ", " ", " ", "OVEN TEMPERATURE SET POINT "

    "V4000 ", " ", " ", "Minutes Left "

    "V4002 ", " ", " ", "Hours Left "

    "V4004 ", " ", " ", "Oven timer preset "

    #END

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: November 02,2007

    Created by: Bob S BN

    Kevin, I didn't import this to try, but these changes might help. Perhaps C0 wasn't on when you wanted to see values. Also, once seconds are converted to minute, you only need to divide by 60 to get hours.

    // Rung 9

    // Address 43

    STR C0 change C0 to sp1, always on

    LD V4004

    SUB TA2

    DIV K600

    OUT V4000

    // Rung 10

    // Address 48

    STR C0

    LD V4000

    DIV K600 change k600 to k60

    OUT V4002

    Good Luck, Bob

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 21,2008

    Created by: Tanno

    Could someone help me with this to run a DL05?

  • adccommunitymod (AutomationDirect)

    Created Date: March 21,2008

    Created by: milldrone

    Tanno,

    I can't help you because rung # 3 uses binary to real and real to binary instructions both of which are not supported by the DL05. But the good news is. If you post what you need,(are you using an eztouch?)(are you trying to make a 2 hour timer?) maybe somebody smarter than myself can help.

    Vaughn

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 22,2008

    Created by: Tanno

    I need a count-down timer that works on the DL05 and the EA7-S6C C-More panel.

    I 've tried and tried and tried. I'm new to PLC programming. I'm doing this one from scratch....never done that before.

    I 've tried using the UDC in DirectSoft32 4.0 and no luck. It doesn't work like the manual and online instruction say.

    So, I tried using a standard timer and subtracting the entered value from the timer value and I get numbers, but not accurate and they are all over the place.

    I 've divided it by 10, 100, 60....nothing it getting me what I need.

    I'll probably start a new thread asking for this because it doesn't have to do with the 06.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 22,2008

    Created by: hanziou

    Tanno,

    I have only used the EZ-touch panels (not the C-more) but something that you may need to check is the number format.

    You say that you are new to PLC programming. Do you understand BCD numbers? If you display BCD numbers as if they were 'binary ' numbers, then it will seem that your subtraction is inaccurate.

    The Koyo (Automation Direct) PLCs use BCD for timers, counters and native math. When you create tags for the HMI be sure that you specify that they match the format of the Vmem* that you are looking at. That should be an editable property of tag. (Also make sure that display object in the HMI uses the correct fromat.)

    *Vmem is a container only. You can look at/use the value in a particular Vmem (e.g. v2000) as binary, or BCD, or bits, etc. Just make sure that you use it consistently.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 22,2008

    Created by: Tanno

    Yes, that's what I 've done. I 've made sure that BCD was and is used everywhere.

    Exception: Input for time is entered by typing in the number. And I'm unsure of the format that it's using.

    The other thing, I finally got a countdown timer to work that's accurate. BUT, I can't seem to get the secs to roll over to mins and visa-versa. And the only way I could think of getting it working is I had to setup a "loading " sequence. This loads the UDC with the value that I want to countdown.

    Is there a faster way to load this? I'm using sp5 (.01 secs) as the rate to load it.

    At the moment, I only have one input for time and I'm using that for the secs. I haven't yet figured out any more of it.

    FYI, I 've been at this for 12-hrs straight for the last three days.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 22,2008

    Created by: Tanno

    Well, here's what I 've got so far.

    PLC 05

    // Rung 1

    // Address 0

    #BEGIN COMMENT

    "Start loading counter until it equals input vlaue (V1400). "

    #END

    STR X100

    ANDN CTA0 V1400

    ANDN X101

    OUT C5

    // Rung 2

    // Address 5

    #BEGIN COMMENT

    "Generating load pulse. "

    #END

    STR C5

    OR CT0

    AND SP5

    ANDN CT0

    OUT C2

    // Rung 3

    // Address 10

    #BEGIN COMMENT

    "Generating count pulse. "

    #END

    STR SP4

    AND X101

    OUT C1

    // Rung 4

    // Address 13

    STR C2

    STR C1

    STR X102

    UDC CT0 K300

    // Rung 5

    // Address 19

    #BEGIN COMMENT

    "Compare current count value with input value (V1400) and stop loading cycle when "

    "equal. "

    #END

    STRE CTA0 V1400

    OUT C6

    // Rung 6

    // Address 22

    #BEGIN COMMENT

    "Compare current count value and stop count cycle when equal to 0. "

    #END

    STRE CTA0 K0

    OUT C7

    // Rung 7

    // Address 25

    #BEGIN COMMENT

    "Convert current count value (CTA0) to minutes. V1200 is the value to display as minutes. "

    #END

    STR SP1

    LD CTA0

    DIV K60

    OUT V1200

    // Rung 8

    // Address 29

    END

    // Rung 9

    // Address 30

    NOP

    #BEGIN ELEMENT_DOC

    "UB ", "co ", " ", " "

    "X100 ", "Load Start ", " ", " "

    "X101 ", "Count Start ", " ", " "

    "X102 ", "Count Reset ", " ", " "

    "C1 ", "Count Pulse ", " ", " "

    "C2 ", "Load Pulse ", " ", " "

    "C5 ", "Load ", " ", " "

    "CT0 ", "Counter ", " ", " "

    #END

    Expand Post