adccommunitymod (AutomationDirect) asked a question.
Power demand for OP 613
Created Date: November 18,2006
Created By: Spidertech
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I am using the OP 613 interface with a DL06 PLC. The OP manual says the 613 has a 20 millisecond in rush current of 1.5A on the 24 VDC supply. Can the 24V power supply included in the DL06 handle this? Or should I purchase a separate 24V supply?
Created Date: November 20,2006
Created by: Tech Guy
The power supply on the DL06 will not be suuitable for the OP-613. For an inexpensive open frame power supply, you might look at the FA-24PS .
Created Date: November 18,2006
Created by: Spidertech
I am using the OP 613 interface with a DL06 PLC. The OP manual says the 613 has a 20 millisecond in rush current of 1.5A on the 24 VDC supply. Can the 24V power supply included in the DL06 handle this? Or should I purchase a separate 24V supply?