I am trying to hook up a 6 " CMore to an Emerson CT UniDriveSP drive. I need a cable to hook the two together. The UniDrive uses a RJ45 connector and MODBUS RTU to communicate. Does AD have a cable already made and if not, what should the pin out be?
Created Date: August 22,2006
Created by: HMI Eng
http://web4.automationdirect.com/static/manuals/eauserm/ch2.pdf page 2-19 will give you the pinout. What cable you make up depends on whether you are using RS232/422/or 485.
Created Date: August 22,2006
Created by: bcarlton
The pins looking INTO the Unidrive SP are numbered 1 at the top to 8 at the bottom. The relevant pins are 2 = RXTX+, 3 = Common, 7 = RXTX-. It is RS485. Communication is 19200,N,8,2. The Modbus addresses ar formed from the menu and item. MM.II The form would be 4MMII. Menu 3 Item 8 (3.08) would be 40308. Even a binary (On/Off) parameter is still a number with either 0 or 1 in it. Hope this helps.
Created Date: August 23,2006
Created by: Dougster
Thanks to both of you for your help.
Created Date: November 27,2012
Created by: burnthills
C-More to Unidrive Ethernet?
Has anyone successfully managed to get the ethernet to work between these two? Both, AutomationDirect and Control-Techniques customer support is telling me all the settings and wiring is right but I get a time out during communication or communication test.
http://www.automationdirect.com/adc/Shopping/Catalog/Operator_Interfaces/C-more_Touch_Panels/C-more_Touch_Panels_(6_inch_only)/EA7-S6M
http://www.galco.com/buy/Control-Techniques/SP2402-LED
In C-More Programming Software
Automation Direct ECOM Ethernet DL05/06/205/405
Module Name: SM-Ethernet
IP Address: 192.168.1.100
Retries 3
Timeout Time 1
Poll Time 0
In the C-More Panel Ethernet Test
Ping Test
D1 Reply from PLC: bytes 32 time 1ms TTL 60
D2 Reply from PLC: bytes 32 time 1ms TTL 60
D3 Reply from PLC: bytes 32 time 1ms TTL 60
D4 Reply from PLC: bytes 32 time 1ms TTL 60
Protocol Test
D1 protocol test failed
D2 protocol test failed
D3 protocol test failed
D4 protocol test failed
Created Date: November 27,2012
Created by: bcarlton
Automation Direct ECOM Ethernet DL05/06/205/405
This would be used to speak to an AutomationDirect ECOM unit in a PLC
Use 'modicon Modbus TCP/IP Ethernet ' to speak directly from the CMore to the Control Techniques drive.
Created Date: August 18,2006
Created by: Dougster
I am trying to hook up a 6 " CMore to an Emerson CT UniDriveSP drive. I need a cable to hook the two together. The UniDrive uses a RJ45 connector and MODBUS RTU to communicate. Does AD have a cable already made and if not, what should the pin out be?