adccommunitymod (AutomationDirect) asked a question.

C-More to Control Techniques UniDriveSP

Created Date: August 18,2006

Created By: Dougster

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am trying to hook up a 6 " CMore to an Emerson CT UniDriveSP drive. I need a cable to hook the two together. The UniDrive uses a RJ45 connector and MODBUS RTU to communicate. Does AD have a cable already made and if not, what should the pin out be?


  • adccommunitymod (AutomationDirect)

    Created Date: August 22,2006

    Created by: bcarlton

    The pins looking INTO the Unidrive SP are numbered 1 at the top to 8 at the bottom. The relevant pins are 2 = RXTX+, 3 = Common, 7 = RXTX-. It is RS485. Communication is 19200,N,8,2. The Modbus addresses ar formed from the menu and item. MM.II The form would be 4MMII. Menu 3 Item 8 (3.08) would be 40308. Even a binary (On/Off) parameter is still a number with either 0 or 1 in it. Hope this helps.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 23,2006

    Created by: Dougster

    Thanks to both of you for your help.

  • adccommunitymod (AutomationDirect)

    Created Date: November 27,2012

    Created by: burnthills

    C-More to Unidrive Ethernet?

    Has anyone successfully managed to get the ethernet to work between these two? Both, AutomationDirect and Control-Techniques customer support is telling me all the settings and wiring is right but I get a time out during communication or communication test.

    http://www.automationdirect.com/adc/Shopping/Catalog/Operator_Interfaces/C-more_Touch_Panels/C-more_Touch_Panels_(6_inch_only)/EA7-S6M

    http://www.galco.com/buy/Control-Techniques/SP2402-LED

    In C-More Programming Software

    Automation Direct ECOM Ethernet DL05/06/205/405

    Module Name: SM-Ethernet

    IP Address: 192.168.1.100

    Retries 3

    Timeout Time 1

    Poll Time 0

    In the C-More Panel Ethernet Test

    Ping Test

    D1 Reply from PLC: bytes 32 time 1ms TTL 60

    D2 Reply from PLC: bytes 32 time 1ms TTL 60

    D3 Reply from PLC: bytes 32 time 1ms TTL 60

    D4 Reply from PLC: bytes 32 time 1ms TTL 60

    Protocol Test

    D1 protocol test failed

    D2 protocol test failed

    D3 protocol test failed

    D4 protocol test failed

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: November 27,2012

    Created by: bcarlton

    Automation Direct ECOM Ethernet DL05/06/205/405

    This would be used to speak to an AutomationDirect ECOM unit in a PLC

    Use 'modicon Modbus TCP/IP Ethernet ' to speak directly from the CMore to the Control Techniques drive.

  • adccommunitymod (AutomationDirect)

    Created Date: August 18,2006

    Created by: Dougster

    I am trying to hook up a 6 " CMore to an Emerson CT UniDriveSP drive. I need a cable to hook the two together. The UniDrive uses a RJ45 connector and MODBUS RTU to communicate. Does AD have a cable already made and if not, what should the pin out be?