adccommunitymod (AutomationDirect) asked a question.

EtherNET IP

Created Date: February 03,2006

Created By: gsu

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hi, I'm relatively new to the field, so I'm still learning. I have a C-More and I am trying to use EtherNET/IP to communicate with a CompactLogix PLC. I'm trying to enter a Tag in the C-more Programming software, but I don't know the syntax to use for the PLC address portion. ANy help would be appreciated.


  • adccommunitymod (AutomationDirect)

    Created Date: February 05,2006

    Created by: TechJunki

    In RsLogix 5000 the first thing that needs to be done is to add your ENBT module to the I/O Configuration Then right click on the ENBT module in the I/O configuration and add new module and then select Generic Ethernet Module. Enter the appropriate IP address and set up the size of words that you will want to use. I believe 250 words is the maximum, for both Input and Output. The default Assembly Instances have worked for me which are Input Instance=1, Output Instance=2 and Configuration Instance=4. After accepting this you will see in your controller tags that Logix 5000 has made the tags for you to use for the HMI. IN C-More basically you have a choice of "I " Input or "O " Output for a data type. These will corespond in direct relasionship with the Input and Output tags created for you. For Example if one of the words Logix 5000 created were something like C_More:O.Data .0 then in the C-More software I would select O data type, 1 would be the address "first word " and bit would be 0

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 06,2006

    Created by: gsu

    Thanks for the help

  • adccommunitymod (AutomationDirect)

    Created Date: February 03,2006

    Created by: gsu

    Hi,

    I'm relatively new to the field, so I'm still learning. I have a C-More and I am trying to use EtherNET/IP to communicate with a CompactLogix PLC. I'm trying to enter a Tag in the C-more Programming software, but I don't know the syntax to use for the PLC address portion. ANy help would be appreciated.