adccommunitymod (AutomationDirect) asked a question.

EZ-Touch tags

Created Date: January 01,2004

Created By: RLCampbell

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am new at programing and using PLC's. I am having no luck in Tagging an EZ-touch Panel toggle switch to activate a PLC input. What is the proper address to activate say Input x1. We have a 260 PLC. Thanks for any help


  • adccommunitymod (AutomationDirect)

    Created Date: January 01,2004

    Created by: RLCampbell

    I am new at programing and using PLC's. I am having no luck in Tagging an EZ-touch Panel toggle switch to activate a PLC input. What is the proper address to activate say Input x1. We have a 260 PLC. Thanks for any help

  • adccommunitymod (AutomationDirect)

    Created Date: January 01,2004

    Created by: bcarlton

    You can't use the display to change an input, these are updated each scan by the PLC from the actual physical inputs themselves. Let the display change V registers and C points. If using bits, be sure to allocate groups of 16 bits starting on a 16 bit boundary (C0-C17, C20-C37 etc). Treat the groups as 'PLC write only ' or 'display write only '. If you intermix them you'll get problems. (Though sometimes I'll clear a group of the 'display write only ' bits on 'first scan '.)