adccommunitymod (AutomationDirect) asked a question.

EZ touch panels-changing screens trouble?

Created Date: April 01,2003

Created By: cdobis

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Is it me, or do others have trouble switching screens on the EZ panels through the PLC? I have a DL205, with a 260 CPU. I want to put up warning and error screens when the occur, however, I seem to be able to get them to work one time, then never again. I am using the EZ touch software Project Attributes to setup my "change screen " variable, then LD that value and output it to variable. What am I doing wrong? Thanks, Craig in Plymouth, Michigan. http://forum1.automationdirect.com/board/confused.gif


  • adccommunitymod (AutomationDirect)

    Created Date: April 01,2003

    Created by: cdobis

    Is it me, or do others have trouble switching screens on the EZ panels through the PLC? I have a DL205, with a 260 CPU. I want to put up warning and error screens when the occur, however, I seem to be able to get them to work one time, then never again. I am using the EZ touch software Project Attributes to setup my "change screen " variable, then LD that value and output it to variable. What am I doing wrong?

    Thanks,

    Craig in Plymouth, Michigan. http://forum1.automationdirect.com/board/confused.gif

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 01,2003

    Created by: cj

    That part works on a "transition ".

    In other words, it needs to see a value change. So if you do a LD of "3 " and OUT to the variable for that part, it will change to screen 3. It will not change to screen 3 again until it sees the number in that variable change.

    What I usually do is to wait for a second or so after I change the value in the variable and then LD a value of "9999 " (number higher than any screen that exist) into the variable in order to allow it to change for my next screen change.

    Hope that makes sense.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2003

    Created by: joev

    Another possibility I have used is to command the screen number change (to 3 for example). Then watch the register that returns the current screen number. When it shows 3, switch the command register to an out of range value (9999 as in previous example). Actually I used 999 as I was afraid that an out of range value would cause an error. I did not program anything to 999. Guess I picked up a tip here too! I found that my code for the switch to the out of range value does not have to be attached to the change screen logic. Just compare the current screen register to the command register, if equal change the command register to the out of range value. This one rung takes care of as many screens as you can switch to! I put mine at the top of my program, but it should work anywhere you put it.

    Expand Post