I'm attempting to connect and EZTouch panel to a DCM within my 205 system (controlled by a 250 processor). The nearest I can get is a message on the display stating: "Protocol Error ". The NAK and ENQ leds on the DCM flash about once a second. I 've created a cable shown on pg 44 of the EZTouch hardware manual which is equivalent to P/N EZ-4CBL-2 Any ideas?
Created Date: June 05,2001
Created by: sjstein
I'm attempting to connect and EZTouch panel to a DCM within my 205 system (controlled by a 250 processor). The nearest I can get is a message on the display stating:
"Protocol Error ".
The NAK and ENQ leds on the DCM flash about once a second.
I 've created a cable shown on pg 44 of the EZTouch hardware manual which is equivalent to P/N EZ-4CBL-2
Any ideas?
Created Date: June 20,2001
Created by: SJI
I am using an EZ-2CBL-1 cable to connect to port 2 on a 250 processor and writing to a V-Memory location in the ladder to change screens.
This works perfectly when the CPU switch is in TERM and I set RUN via DirectSoft. If I place the CPU switch in RUN I get PROTOCOL ERROR on the EZ-TOUCH http://forum1.automationdirect.com/board/frown.gif
The screen does change - before the error actually pops up - and the error goes away after a few seconds, but its really annoying.
Does anybody have any idea what could be wrong?
Created Date: June 20,2001
Created by: tweedy
TERM stands for terminal mode or better yet, communications mode. Any terminal can talk to the CPU when selected. DIRECTSOFT, DSDATA, handheld programmers, touchscreens will not work unless TERM is selected. I use the RUN position on fixtures I don't want people to accidently modify.
Created Date: June 20,2001
Created by: tweedy
Have you written some RLL to do your DCM network communication to the screen? (ie RX & WX) The DCM will NOT drive a device by itself. I assume your 250 ports are full and that's why aren't you using the 250 CPU to run the screen. But if a port is available that's where you should put it.
Originally posted by sjstein:
I'm attempting to connect and EZTouch panel to a DCM within my 205 system (controlled by a 250 processor).
Created Date: June 20,2001
Created by: SJI
Thanks tweedy. I should have figured that out. We make industrial equipment and I guess I'm just too used to putting the switch in RUN. Again thanks for the quick response.