adccommunitymod (AutomationDirect) asked a question.

Modbus Simulator

Created Date: January 24,2008

Created By: teritask

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Can any suggest a Modbus TCP/IP simulator so I can try to communicate with my CMore via Modicon Modbus? I'm still at a loss as to how to communicate with my CMore through Modbus Ethernet. My post from a few days ago details what I'm trying to do using Labview. Thanks for any help.


  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: OpZed

    Modbus Slave from www.modbustools.com seems to work very well. It has serial and ethernet modes. The demo is time limited to 10minutes per session I think.

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: teritask

    Thanks...I just downloaded it a few minutes before I received your reply. I still cannot connect to the CMore. This is driving me nuts! It seems like it wants to be connected to a PLC only. I have the PLC-001: PLC Communication Timeout error message up in the corner also. I know it's not a grounding issue...already been checked out.

    I hope I don't have to scrap the idea of using a CMore because I really like easy they are to program and it looks nice on the machine I'm designing. I have to get this job shipped next week so I'm kind of in a crunch situation.

    I downloaded just about every modbus simulator I could find but none of them communicate with the CMore.

    Time to switch my searching to Labview compatible touch screens! (I don't like the ones NI offers).

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: jackson

    I just connected C-more to Modbus Slave from www.modbustools.com. Works like a charm.

    Can you post your exact settings for both sides?

    IP addresses, settings, etc...

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: teritask

    Which one did you use, Modbus Slave or Modbus Poll?

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: OpZed

    Modbus Slave

    C-more is a modbus master, it sends requests out and expects replys back from the slave devices.

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: teritask

    CMore settings: (forgot you cannot attach files in this forum)

    PLC Protocol: Modicon Modbus TCP/IP Ethernet

    IP Address: 130.151.217.5

    PLC Port: 502

    PLC Slave Number: 1

    all the rest are the default settings

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: teritask

    That's the one I'm trying to use. The only setting for TCP/IP is the port, which I set to 502.

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: teritask

    I get the error message:

    Modbus/TCP Connection Failed: bind-error 10048.

    I also tried the Master one which didn't work either. Am I missing a setting in the CMore? I still have the PLC timeout error at the top of the screen. Like I said, I know it's not a grounding issue.

    Thanks.

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: OpZed

    Are you programming C-more through USB or Ethernet? What is the IP address/Subnet Mask of C-more? Can you ping the C-more IP from your PC?

  • adccommunitymod (AutomationDirect)

    Created Date: January 24,2008

    Created by: teritask

    Ethernet. Yes, I can ping the CMore.

    I have 3 items on my network hub (no internet):

    Computer: 130.151.217.4

    CMore: 130.151.217.5

    PXI: 130.151.217.2

    Subnet mask: 255.255.255.0 on all.

    I noticed the Port info in the CMore also has:

    Default gateway: (blank)

    DNS Server: Automatically

    Can these settings be a problem?

    Expand Post