rjm21 (Customer) asked a question.
I have several CLICK Ethernet PLC and EA3-T4CL combo systems running. I've never had communication issues between the PLC and HMI until now. We recently purchased an EA3-T4CL (We'll name this HMI1) and a C0-12DD1E-D to communicate together via ethernet. The HMI1 will not connect, always showing the P001: PLC COM Time Out error. Changing the IP Address and/or the TCP port makes no difference. I have verified that the HMI1 is set to communicate to the correct IP address and TCP port via the PLC protocol Automation Direct CLICK Ethernet.
I took this HMI1 and tried to connect it to two other Click Ethernet systems (HMI 2 and HMI3, also EA3-T4CLs) that are currently successfully communicating with their own EA3-T4CL's. The new HMI1 would not communicate, still giving the P001 error.
I also took the HMI2 and HMI3 from the two working Click Ethernet systems and was able to get them to communicate with the C0-12DD1E-D. This leads me to believe there is a problem with the new HMI1.
One thing I've noticed is on a successfully communicating Ethernet system, the PLC's Green Ethernet port light will flash rapidly. When I use this new HMI, the PLC's Ethernet port lights will not flash, but stay lit up solid green and amber.
I then restored this new HMI1, uploaded a successful program that is communicating with a BRX PLC via Ethernet. This worked. So I took the HMI (HMI4) that was previously connected to the BRX, uploaded a CLICK program and changed all the necessary settings, and could not get this one to connect to any of the CLICK ethernet PLCs. Same issue as HMI1.
I have a small hunch that the CLICK Ethernet PLC Protocol is not being successfully transferred to the HMI. All PLCs and HMIs are running the newest firmware revisions.
I have quadruple checked that the PLC protocol, TCP port, and IP address are correct in both the C-more programming software and Click programmnig software. I've tried using different PC's and different Ethernet cables as well.
Can you think of anything that I'm missing?
What version Software are you using?
We found an issue in 4.35 with the power up ARP announcement on the EA3 Ethernet. This was corrected in version 4.40.