JER (Customer) asked a question.
DO-more BRX plc connected via eithernet to Kepware OPC server, I don't see drivers listed. Am i missing something.
Basically trying to connect WX data over the nextwork. We have a bunch of DL260 and they work great.
Basically trying to connect WX data over the nextwork. We have a bunch of DL260 and they work great.
Hi JER,
The Do-More series will use Modbus TCP to connect to Kepware OPC server.
https://www.kepware.com/getattachment/93f6f654-14e4-49f3-a7ad-71d11825c8d3/connecting-to-a-modbus-ethernet-device-guide.pdf
The memory locations that are available for Modbus are:
MI0 to MI1023 - Input Bits
MC0 to MC1023 - Output Bits
MIR0 to MIR2047 - Signed Word
MHR0 to MHR2047 - Signed Word
Tech support helped me out when I was connecting AdvancedHMI to the BRX PLC.
https://accautomation.ca/brx-plc-advancedhmi-communication-modbus-tcp/
I hope this helps you out.
Regards,
Garry
https://accautomation.ca/series/brx-do-more-plc/
Just to verify are you using Automationdirect KepDirect OPC or Kepware KepServerEX? What version of the software are you using?
What driver package do you have installed if using KepServerEX?
AutomationDirect Suite?
Modbus Suite?
This will determine what instructions will be needed to communicate to Kepware.
Thanks for the help Garry I will look into that a little deeper. I'm still a little new at do more do I will try and connect the dots.
how would element WX1 on do more for instance line up in modbus? they would just be V memory locations in DirectSoft
We currently just have the AutomationDirect Suite on KepServerEX
Thank you!
Hi JER,
The following post will explain the memory areas in the BRX.
https://accautomation.ca/brx-plc-numbering-systems-and-addressing/
When using Modbus only the addresses mentioned above have the ability to read and write. So you would move WX1 to MHR area to allow modification / reading.
Since you are using the AutomationDirect Suite on KepServerEX, I would wait for some more answers from ADC_Community_02.
Regards,
Garry
Since you only have the AutomationDirect Suite installed & looking at Kepware's site they do not have driver for Do-more available. Modbus is another driver suite separate from AutomationDirect drivers.
Let me get in touch with our Communications Group and see what options are available for you to get you up and going.
You will need to use the AutomationDirect ECOM driver in KepServerEX and then target the DirectLOGIC memory blocks. (reference DMD0251 help topic). In addition the available memory blocks available are listed in the table in help topic DMD0206 for Built In Data Blocks.
Thank you everyone for your help, i was able to get it going with Ecom setup. I will dive more into this later. Is there any plan for native Kepware drivers like DS? we have over 500 OPC tags in the factory and that alot of instructions to write... if we were to go to more do more setups. The DS integrate really well.
Thank you!
Don't know if Kepware is planning on any additional drivers. You may want to reach out to them.
Another option is to use our Productivity PLC as an alternative since it does have a native driver in KepServerEX.