MoneyMetal (Customer) asked a question.

No input with proximity sensor on Click C0-00DR-D

I have my prox sensor wired correctly for PNP and I get the lights on the sensor to light when I need to, But I am not getting an input on my Click PLC. I have brown to 24v, blue to 0v and black to control. Any help would be appreciated.

 

Thanks.


  • Adisharr (Customer)

    Make sure you have C1 and C2 on the Click attached to your DC common. Also check the voltage output on the sensor itself.

  • MoneyMetal (Customer)

    Yes! thank you very much. Most of my experience has been with Beckhoff, and that is mostly just installing.

    • MoneyMetal (Customer)

      Thanks Garry, I did watch a bunch of your videos and hang out on that website for a bit before I started. The main thing was when I ordered the click, I didn't know what type of sensors I would have been using, so I ordered the relay vs the sinking or sourcing PLC. The problem was not with wiring the sensors, but with not having the common connections for the inputs and outputs.

      • Garry (Customer)

        Thanks for the update MoneyMetal.

        Garry