First program with Shift Register

When I check syntax after adding a shift register, it complains about C0202 and C0003 in my shift register rung. I see lines and have no place to insert a coil. What am I missing?


  • Nebr. Tech (Customer)

    There is no coil, the shift register is the output instruction. The register addresses should be contiguous locations, and it may not like leading zero;s.

    • mtczapla (Customer)

      Yes. I know there is no coil. But the C error code is complaining about a missing coil. It makes no sense.

      Inside the shift register, I entered a start bit of C2 and end bit of C8. No zeros.

  • Todd Dice (Customer)

    Are there inputs connecting to all three inputs of the shift register?

    • mtczapla (Customer)

      Yes.

      Data connects to some X inputs.

      Clock connects to 1sec clock SC7.

      Reset connects to 1st scan SC2.

      • Todd Dice (Customer)

        My only recommendation is if you could screenshot an image of your code and attached it here.

  • Nebr. Tech (Customer)

    I have entered a program on my Click software similar to your description. No errors shown.

    Is there a way for you to Email or upload a copy of your program?

  • ADC Community_04 (AutomationDirect)

    Click on the Shift Register and tap your left arrow key to cycle backwards through the rung. Verify there are no breaks in any of the legs (Data/Clock/Reset). C0202 is a missing line connection (a break in the rung).

    C0003 will occur if you have a contact on a rung that doesn't terminate to the output column, which would also happen via a break in the rung.

    • ADC_Tech_03 (AutomationDirect)

      I agree with 04. When I loaded your program I found that the clock input was not connected on the shift register instruction. This may not show on a smaller screen and you might spot it by using the scroll bar at the bottom of the logic window. ​