J2 (Customer) asked a question.

Can the node red module read input valves from another click plus plc on the same network or does it need to be done with modbus.

  • ADC_Tech_03 (AutomationDirect)

    It's possible, but reading valves over Modbus TCP would be the simplest method if that is all it would be doing.

  • J2 (Customer)

    Thanks for the info. No control needed just looking to get some numbers up to Blynk's cloud.

  • ADC_Tech_03 (AutomationDirect)

    If you're trying to send data to Blynk then Node-Red is a good option for the job. If the job is just to send data from PLC-A to PLC-B alone on the same network, not so much.

  • J2 (Customer)

    Yes that is the plan. Just wasn't sure if I could use a click read node to read a address in PLC-B with the node red module in PLC-A.

    • ADC_Tech_03 (AutomationDirect)

      Unfortunately, the Click Read and Write nodes only work with the controller that Node is running on.