Hello,
I have a sourcing output from a standard output (Not High Speed) on the BRX and using the PWMOUT command. The source Voltage is 5V. I measure 5V from a neighboring active output (not PWM) to com/System ground. COM on the 5V power supply is connected to the system ground.
If you notice on the scope that the pulse does not drop to 0V but somewhere around 1V. Is this to be expected? Thanks!
I don't know about "expected" but I wouldn't be very surprised.What kind of load do you have on the output? if it is only a 10meg Ohm scope probe I would be at all surprised, the specs for a sourcing BRX output show a minimum output current of 0.1ma, I might try a 1K resistor to ground. If driving a device with an optoisolator input the LED will have a voltage drop that might well be around a volt or more.