
Anugrah Sajan (Customer) asked a question.
I have the current configuration:
These are my Slot 0 setup settings:
These are my UA Expert settings:
This is my PLC's Date and Time settings, which are in the range of the certificate:
This is my small ladder logic program that I write to ensure the PLC is running:
Every time I attempt to connect my PLC's OPC UA server with the UA Expert Client software, I get the following error "Server Node ClickPlusOPCUA Could not connect to Server: Bad Timeout.
I can successfully ping the module
I am connected to the C2-OPCUA module through a network switch and ethernet cable.
The PLC is being programmed via micro-usb.
There is 24V DC supply for the PLC.
I am on the latest firmware of the software and PLC.
Why can I not connect to the OPC UA server through the UA Expert Client software?
I can connect other simulation server software (Prosys) to UA Expert. The C2-OPCUA module is flashing the green OK LED. So, what am I doing wrong here?
When online with the CLICK software is there any PLC Error for Slot0? Also what is the status of SC301, SC302, and SC315. Also SD308. These are status bits and registers for the Slot 0 Module. If no errors are shown you could try to force update the FW for the C2-OPCUA by unchecking the Skip updating modules with the same version button. Please See CL014 and CL340 for these steps.