strantor2 (Customer) asked a question.
GS23 with Ethernet/IP comms card reports status of the digital inputs in word 8. Works just fine as long as I have those inputs assigned to something multi-spd ref or jog or anything else. But as soon as I set the inputs to 0 (no function) their bits no longer change in word 8. There are no options for 2.01-2.xx which are convenient for me to set up. I want the drive's digital inputs to be just generic use, only meaningful to the PLC that the drive is connected to. Is there an option or solution that I am missing?
It's not part of the assembly instance but you could read the state of the inputs via explicit message.
Service code: 0xE
Class: 0x300
Instance: 0x22
Attribute: 0x10
Size: 2 bytes