PADILLA (Customer) asked a question.

How can I connect to an EA1-T6CL HMI?

Image (26)I have a screen of this model, but I have already tried connecting with several versions of the C-more software and none of them can find the screen. Even when I see the port that opens (COM) and select it in the program, it doesn't find it and displays or throws an error.


    • PADILLA (Customer)

      Negative, the HMI is currently running an application. What I want to do is upload (pull) the program from the HMI. Does this model need to be on this screen to do that?

      • Matt Pawlak (Customer)

        I never used that model but I assume it needs to be on that screen for any kind of transfer. Worth a shot anyway.

  • PADILLA (Customer)

    OK, I'm going to try it with the old software version I have, since I tried with the newest version of C-more and it didn't work.

  • Tom@Pton (Customer)

    I didn't think an EA-1 could be accessed via the newest C-more. Different software.

  • Durallymax (Customer)

    Not confident on that model, but should be able to hold F1 and F5 to get it into setup screen and then you can try to connect.

    • Todd Dice (Customer)

      Yeah, I have a hunch the OP is not on the setup screen.

  • daakers (Customer)

    You will need this software to connect to your C-More. "C-more Micro Programming Software"

    Not sure if you can still download it or not. 

  • Tom@Pton (Customer)

    The newest version is 4 years old.