Jimmyy (Customer) asked a question.
L7P drive configuration with Mitsubishi FX3G-40MT/ESS not responding to motion request
The Mitsubishi FX3G-40MT/ESS is PNP Pulse output, the driver does not respond to the pulse output.
If the PLC is connected directly to the motor, the pulse would turn the motor.
Is there a configuration file or better documentation, because the current documentation does is not clear about PNP config. Reference the PNP config but it does not run.
Though they don't show a PNP example in the manual, it should work. A wiring example would be as shown
https://cdn.automationdirect.com/static/manuals/lselectric/l7p200vmanual.pdf#page=140
If you are sending a second PNP signal, it would use same concept, except using the PR+- terminals
You also want to reference 6.1 in the manual for setting the pulse input logic function (Index: 0x3003).
https://cdn.automationdirect.com/static/manuals/lselectric/l7p200vmanual.pdf#page=192