z28z34man (Customer) asked a question.

3ACTR to P1-08ADL-1 wiring

The manual for the 3ACTR isn't 100% clear but would I be correct in assuming + terminals 1, 3, 5, and 7 gets connected to +24V and - terminals 2, 4, 6, and 8 get connected to the P1-08ADL-1 inputs. Terminals 9 and 10 go to 24V and com and are not polarity sensitive

 

https://cdn.automationdirect.com/static/specs/acuamp3act3actr.pdf

 

https://cdn.automationdirect.com/static/manuals/p1userm/inserts/P1-08ADL-1.pdf


    • z28z34man (Customer)

      Do I disregard

       

      "Note: Power supply and output signal ARE NOT isolated. Do not connect the negative terminals to a common point."

       

      and wire 2, 4, 6, and 8 to 24 com

      • ADC Community_02 (Automationdirect.com)

        This just means that there is no isolation between the power input (terminals 10 and 9 are the power supply terminals) and the output terminals. As long as you are wiring to your PLC input card directly there should not be any issues. If you are using the same power supply there is a risk of ground loops that could mean the signal would be incorrect because some of the current could flow through a different path (ground loop). Won't be an issue if you have your output loop wired directly to an analog input card.

         

        If using the same power supply for the analog input module and the Acuamp I would put the output of the AcuAmp before the input card. So 24V to the AcuAmp and the negative side to the input of the card. The current would flow through the card and out the 0V side of the card to the power supply. Should not have any ground loop issues that way.

        Expand Post
      • z28z34man (Customer)

        production finally gave me the down time to install this and i am not getting a good signal from the AcuAmp transducer.

         

        I wired it like the attached print and got over range on all channels. Not wanting to damage the P1-08ADL-1 card popped off the termina block from the card. i then removed the wire from terminal 2 (analog input 1) added a meter and 200 ohm resistor and am reading 82ma.

        Expand Post
        • acuamp
      • z28z34man (Customer)

        I changed it to where pins 2, 4, 6, and 8 are tied to 24com and pins 1, 3, 5, and 7 go to the inputs and it appears to be reading correctly now

      • kewakl (Customer)

        Timely post. We seems to be having some issue with our transducer installs.

        Currently, I have no more details.

         

        Thank you for posting your resolution.

      • z28z34man (Customer)

        An isolated input card would probably have been better but it appears to be working fine as is.

         

        I do know if an isolated input card is on the road map for the P1 series as the P2 series just got the P2-08ADS-1 last month.