TamNg (Customer) asked a question.
I am working on a project with P1-550 plc.
Every time the power turned on, the plc is on stop mode (green led "RUN" is off) even with the toggle switch on RUN! If I turn the switch off, then on, the plc would be on RUN mode ( green led on).
Am I missing something?
Thanks in advance
Please refer to help topic P223 in the Productivity Suite software.
Error code E01802 on your P3-550E CPU indicates a "Retentive Memory error". This is considered a critical error and typically occurs when the CPU's battery is dead or missing. The retentive memory stores data that should be preserved through power cycles, and without a functioning battery, this data can be lost or corrupted at startup."
Recommended Action:
If the error persists after replacing the battery and cycling power, further investigation may be required, but in most cases, battery replacement resolves the issue.