htmatrix (Customer) asked a question.
P2K
Has anyone experienced using Terminator I/O with P2K as remote?
Is there any EDS file available for Ethernet I/P Client setting for Terminator I/O, or
should I use MRX / MWX instructions?

htmatrix (Customer) asked a question.
Has anyone experienced using Terminator I/O with P2K as remote?
Is there any EDS file available for Ethernet I/P Client setting for Terminator I/O, or
should I use MRX / MWX instructions?
Copyright © 1999-2023 AutomationDirect. ALL RIGHTS RESERVED
If you are using a T1H-EBC100 with P2000 then only option is to us MRX/MWX instructions:
Thank You!
I was asked to convert one of the old PLCs to integrate with all IP environment with minimum HW change; Protos was my favorite option to achieve this, but I figured that Protos is limited only with sinking IOs. Terminator was another option, but Terminator project became more expensive for 32 each I/O remote than a configuration of 4 slot BP + P2K + 32 In P2-NE + 32 out P2 - T.