Zedsdead (Customer) asked a question.
SS2 Pro Software EDS file generator questions
Hello, I've built a single axis machine using the SS2 drive platform with modbus TCP. I'm now designing a dual axis version and have decided to switch to EIP comms in the process. I configured the i/o assembly objects in SS2 pro and generated the file. When i loaded that into my PLC there were some things i did not expect. I apologize in advance as this will be my first implementation of EIP comms so i'm somewhat a noob.
- The data type for all parameters was set to 32B UINT (hex code 0xC8). For PR path parameters (Definition and data), DATA is actually a 32B INT (signed) (hex code 0xC4). I don't think the UINT type will work correctly if my data is negative (ie) reverse direction, Is that correct?
- In the EDS file the section for parameters min, max, default values is 0,0,0. Why does it not fill in the correct range? Does that matter?
- The EDS file did not include [Connection Manager] or [Connection Configuration] objects. I'm wondering if that is normal or if it is because i have not set up EIP related parameters in SS2 pro or installed a physical EIP comm card yet?
- The EDS file did not include a configuration section for the assembly object yet my controller (Unilogic) interpreted it and created it anyway. The config section is shown in the SS2 manual pg 9-26 at 96 words. Does the SS2 drive make any use of this or not? For example i'm wondering if I might somehow use this to disable NV writes (par P2.030).
- Is there any way to adjust the data length for the I/O assembly or is it fixed to the 16 x32B inputs and 16x32B outputs. You'll note that for unused parameters its the default P0.0 -Firmare version. I don't need that and certainly not multiple copies of it but if there is no way to reduce the data length i'm thinking i may as well include some other parameters that i would normally just use explicit messaging for (ie) config settings or non-time sensitive stuff like P2.030 -Disable NV writes
generated EDS file attached,
Thank you
If you would like to disable writing to non-volatile EEPROM, be sure to include parameter P2.030 in the "O->T PLC Output Values" table in the SureServo2 Pro's EtherNet/IP setup. Then use the corresponding Output Data element in your PLC to write a value of 5.
As you have discovered, the default parameter selection is P0.000, which returns the Firmware Version. I cannot imagine that any user would need the firmware version value on a cyclic basis. A more appropriate default selection for unused parameters, in my opinion, would be the "Monitor Item: [0xFFFF]<empty field>" selection option that is available.
In hopes of addressing your other questions:
I hope this information helps you move forward in your project.
Thank you for the prompt reply.
Thanks
Regarding point 1:
Please check your UDINT value. You list a result of 4,203,967,296. However, the result SHOULD be 4,293,967,296. Other than what I suspect is a typo, I think you now have an understanding of this. The following values all have the same bit pattern:
Regarding point 4:
The SureServo2 drive DOES use the data from the Configuration Assembly. The Configuration Data consists of addresses the user has selected for the mapping of the I/O Assemblies. This data is sent to the drive during the establishment of the I/O Messaging connection (called the Forward_Open Request).
Hello, Yes that was a typo, off by three decimals places, good catch😉
Totally understand what you meant about bit pattern now. Thanks that helped.
Oh so the Config assembly is not optional? I thought that would be configured on the drive end using SS2 Pro?
Thanks again