PappyJoe (Customer) asked a question.

Nitra EIP Problem. No Input from PAL-S06.

We have gotten our EIPs back from Automation Direct. I'm testing them. Setting up the first one, I'm able to control the valves and I can set the outputs on the PAL-S07. I cannot see any inputs from the PAL-S06. I downloaded the sample file. I've added the EIPMSG for input assembly instance 101 and transitioning assembly instance 104 to transition from 0 to 1. Not positive I'm doing it correctly. Would appreciate any help with this. If it's possible to talk to someone that would be helpful.

 

Thanks


  • ADC Community_04 (AutomationDirect)

    Looking at the project you sent in to tech support,

    The EIPMSG for inputs (Instance 101) as you have it differs from the example project and is not correct.

    The service should be 14 (Get Attribute) and Use Attribute (0x3) selected as shown.

    You have the service set to 1 (Get All Attributes).

    Please correct these errors and retest.

    EIP_Inst101

    Expand Post
  • PappyJoe (Customer)

    Yes, I noticed that as well after I had sent these. I corrected it and it still didn't work. I did get it working. I created the pgmReadWriteData and copied the previous program we had used. I can now control the valves, digital outputs, and see the digital inputs. A combination of the two programs got it working. Thanks.pgmReadWriteData5pgmReadWriteData4

    Expand Post