PappyJoe (Customer) asked a question.
Using a BRX PLC with the Nitra EIP. I am using the Automation Direct quick setup software. I have ran the setup on the Nitra and have successfully written the setup to the Nitra, confirmed by making X1 on the PAL-SO9 NPN. I didn't change the IP address, made the BRX IP 192.168.192.130 with 255.255.255.0 subnet. I have set up a unit before which is up and running with no issues. I've tried three different EIP units, I've tried three different BRX PLCs. I have used the Ping in the PLC programming to ping the IP and have gotten successful return. It will not turn on the valves or show any inputs to the S06. I have also checked for anything else using the TCP port and it's showing nothing.
@tomm (Customer) @PappyJoe (Customer) ,
This issue has sparked further investigations into the product.
The vendor recently made a change to the Ethernet chip set. The old chip set would report a MAC OUI of 00:02:A2:xx:xx:xx. The new chip set reports a MAC OUI of 14:1A:AA:xx:xx:xx. When notified of the chip set change, we were of the understanding that the behavior of the PAL-EIP functionality was not affected. However, as a result of this investigation, we have found that the PAL-EIP modules with the MAC OUI of 14:1A:AA:xx:xx:xx are NOT behaving the same. Two issues have been found and reported to the vendor:
So, the example code is correct. The process that you have attempted over and over again is also probably correct. This is a firmware issue that you have no control over. The behavior has been reported to the vendor, the vendor is actively working on a solution, and the current stock of PAL-EIP modules has been put on hold until the issue is resolved.
Once new stock is available, please contact AutomationDirect and have these units replaced with updated units.