Tom@Pton (Customer) asked a question.
I have a GS20 on a well pump. I notice that it does not cycle via the wake/sleep settings and at the moment runs almost continuously at the pressure set point. I thought it had been working prior to installing an ethernet card. I may be wrong.
8.06 =46.68 (28 hz)
8.10=42.
8.11=32
Suggestions?
I found several of my brain fault issues.
I had 8.10 & .11 entered as my desired PSIs, not hz,
The pump motor needs to run at a min of 30 hz & I had min set at 30.10 which was above the 28hz.
Clear?
I changed:
8.66=32.2 hz (53.67 psi) Set point
8.10=31.9 (53.17) Sleep
8,11=30,02 (50.03) Wake
It is cycling so I believe I have it correct now. The pressure range is a lot closer than I had anticipated.
Thank you.