MHW (Customer) asked a question.

Will the lugs on a GCB400H-3FF400LL breaker accept two 3/0 copper wires? The specifications only list 700-750kmcl Al.

lugs


  • ADC Community_02 (Automationdirect.com)

    Only 1 wire is allowed per lug. This is the requirements per the UL rating and is provided in the product insert and on the product label. See insert below.

     

    prodcutInsert

    Selected as Best
  • ADC Community_02 (Automationdirect.com)

    Only 1 wire is allowed per lug. This is the requirements per the UL rating and is provided in the product insert and on the product label. See insert below.

     

    prodcutInsert

    Selected as Best
  • MHW (Customer)

    Thanks for the information. I see that the insert shows different information that the specifications. The specs only show AL wire for the 400A breaker.

    Is there someone that sells a parallel lug for this breaker?