SS757 (Customer) asked a question.
I am working with an EA9-T10WCL, and was wondering if there is a way to:
--Transfer a project update without overwriting the recipe values on the HMI (a feature that TIA Portal supports)
or
--easily transfer the recipe values from the HMI into my project.
I know that you can back up the HMI recipes to a flash drive, and import that into the project, but that seems clunky, plus my company doesn't support non-encrypted flash drives, so that isn't a good option for me.
Thanks!
On EA9 the only option is to backup the recipe to a SD card or USB drive. Transfer the project then restore the recipe from the device. This is all done locally through the System Screens.
On CM5 you can use the Data Maintenance tool under the Panel Tab in the software t read the recipe file and then write it back after loading the project.
I understand the the ideal solution would be to have the option to not overwrite the Recipes on a Project Transfer.