Dear all, It happened, that the DL-06 PSU ES-V4431 has died. I have tried to search for a replacement, but unluckily. So I need a little help from you. I need to get the exact voltage measures suppled from ES-V4431 PSU to the PLC board. By having this information, I will try to replace the original power supply with analog. I know, it will be odd, but I need to extract the important data from the PLC memory.


  • adccommunitymod (AutomationDirect)

    Created Date: July 16,2016

    Created by: simmasr

    Dear all,

    It happened, that the DL-06 PSU ES-V4431 has died. I have tried to search for a replacement, but unluckily. So I need a little help from you. I need to get the exact voltage measures suppled from ES-V4431 PSU to the PLC board. By having this information, I will try to replace the original power supply with analog. I know, it will be odd, but I need to extract the important data from the PLC memory.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2016

    Created by: simmasr

    annyone can help here?

  • adccommunitymod (AutomationDirect)

    Created Date: July 19,2016

    Created by: johnaden

    I have a DL06 opened up. Not sure where to check power supply voltages.

  • adccommunitymod (AutomationDirect)

    Created Date: July 20,2016

    Created by: ControlsGuy

    If the data is so critical you'd be willing to repair or replace the power supply, I know where you can buy one. Every 06 comes with one built in!

  • adccommunitymod (AutomationDirect)

    Created Date: July 21,2016

    Created by: johnaden

    Where are you located?

  • adccommunitymod (AutomationDirect)

    Created Date: July 21,2016

    Created by: simmasr

    Lithuania, Europe.

  • adccommunitymod (AutomationDirect)

    Created Date: July 21,2016

    Created by: johnaden

    Please send a larger picture.

  • adccommunitymod (AutomationDirect)

    Created Date: July 26,2016

    Created by: simmasr

    Could anyone measure voltages on these points with highlighted circle, while PSU is in operation? I have attached pictures to the post.

    n102078 n102079

  • adccommunitymod (AutomationDirect)

    Created Date: July 26,2016

    Created by: Szarman

    I'm sure someone can provide you with the voltages, but I would recommend not hooking up a different power supply to it. I would just buy another DL06 and swap the power supplies. The voltages that are generated are more than likely sequenced a certain way, also i would imagine one of those signals on the wire is a reset/power good signal. To get it all to work is definitely possible, but might require a working power supply and a scope to capture the power sequence, and signal levels then creating something to emulate it. If it not done properly, you risk the possibility of damaging the CPU/base/modules.

    Edit: Did you check the fuse? It is the red part on the lower left corner.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 03,2016

    Created by: johnaden

    Here's my measurements In order -

    Black wire: (Reference) Ov,

    black wire, +5 vdc,

    black wire 0 vdc,

    black wire o vdc ,

    brown wire +5 vdc,

    brown wire +5 vdc.

    Expand Post