adccommunitymod (AutomationDirect) asked a question.

H2-DM1E setup Modbus/TCP Server for SICK INSPECTOR Vision Sensor

Created Date: May 02,2013

Created By: JamesB

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am having trouble trying to get a H2_DM1E to my sick inspector I40 has anyone got one communicating Port no is correct as per http://www.chronos-vision.de/downloads/FAQ_Summary_Inspector_V1.05.pdf in the sopas software to setup inspector I get this error; The I/O extension box could not be found on the specified address. The box must be reachable on the specified address for inputs to be read and/or outputs to be set. It will still be possible to configure the Inspector to use the I/O extension box.


  • adccommunitymod (AutomationDirect)

    Created Date: May 02,2013

    Created by: BobO

    The manual claims that it is using UDP, not TCP. Although I think Modbus over UDP is used by a few devices out there, it is not common. Do-more currently only supports Modbus/RTU and Modbus/TCP.

  • adccommunitymod (AutomationDirect)

    Created Date: May 02,2013

    Created by: JamesB

    BobO

    thanks for your reply it is much appreciated

  • adccommunitymod (AutomationDirect)

    Created Date: May 02,2013

    Created by: JamesB

    I am having trouble trying to get a H2_DM1E to my sick inspector I40 has anyone got one communicating

    Port no is correct as per

    http://www.chronos-vision.de/downloads/FAQ_Summary_Inspector_V1.05.pdf

    in the sopas software to setup inspector I get this error;

    The I/O extension box could not be found on the specified address. The box must be reachable on the specified address for inputs to be read and/or outputs to be set. It will still be possible to configure the Inspector to use the I/O extension box.