Ladder logic conversion
Created Date: March 07,2008
Created By: duneman546
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I am upgrading a 340 CPU to a 350. Is there a tool in DirectSoft32 that will do the conversion for me or do I have to do this manually?
Created Date: March 07,2008
Created by: franji1
No, you have to do it manually. However, if you export the program to mnemonic text, most of the instructions convert pretty straight forward
340 doesn't have X/Y, so you would have to change
STR IO0
to
STR X0 (or STR Y0 if output module)
The I/O is done differently since 350 distinguishes between Xs and Ys, so except for the I/O in the first slot, all your I/O numbers will be different.
You'll have similar editing to do with Registers (R vs. V memory) along with the accumulator instructions (don't ask me the equivalent of a DOUT5 is in 350-land http://forum1.automationdirect.com/board/biggrin.gif )
Then you can import the "new " mnemonic text program.
I don't know if it would be easier to print out the program and just re-enter it in ladder, or if you are good with RLL mnemonics, do what I mentioned above.